  #1  
Old February 17th, 2010, 16:08 PST
Arthurs Arthurs is offline
New User
 
Join Date: Feb 2010
Posts: 1
Default Skystream 3.7

I have a Skystream 3.7 mounted on an 80 foot tower. When I first installed it I could not get anything form the generator and a friend with experience said it was because of my grid connection which was a "Y" from the utility which is the typical three phase configuration. I was planning a solar and they said when I got the inverter running that the generator would run. I had to get a single phase grid from the utility to get the Xantrex to lock onto the grid but then the generator started working.

My problem now is that the generator ran about ten days then stopped with a good wind. It had been producing well during those ten days. My location has a steady wind most days.

When I look at the remote it says normal but zero Kwh since it is not turning. I climbed the tower and the blade can be turned easily by hand.

Does anyone have any ideas of what my problem could be. I have written to Skystream customer service by email three times and get no response. From reading the book it appears that the latching relay may need to be reset. Does anyone know what voltage needs to be applied to activate the coil on the latching relay.

Dave
Reply With Quote
  #2  
Old February 18th, 2010, 10:20 PST
guerrillasolarguy guerrillasolarguy is offline
Registered Guest
 
Join Date: Feb 2010
Location: Casper, Wyoming
Posts: 6
Default Re: Skystream 3.7

Quote:
Originally Posted by Arthurs View Post
I have a Skystream 3.7 mounted on an 80 foot tower. When I first installed it I could not get anything form the generator and a friend with experience said it was because of my grid connection which was a "Y" from the utility which is the typical three phase configuration. I was planning a solar and they said when I got the inverter running that the generator would run. I had to get a single phase grid from the utility to get the Xantrex to lock onto the grid but then the generator started working.

Dave
The skystream can be converted to support two legs of a 208 3phase system with a simple click of a computer program by a servicing dealer (you cannot do it yourself). I would not hook up a turbine to power when you are not sure what kind of power you are hooking to (take a meter and measure line-line voltages). You need to call SWWP technical support and walk your problem through with them.

Joel
Reply With Quote
  #3  
Old February 18th, 2010, 14:53 PST
BillF BillF is offline
Registered Guest
 
Join Date: May 2009
Posts: 39
Default Re: Skystream 3.7

If the rotor is turning freely then the latching relay is not tripped. Perhaps the turbine is not quite oriented to catch the wind at lower wind speeds. Check the plumb of the tower and the level of the mounting flange. It has to be perfect for the downwind design of the turbine.

Bill


Quote:
Originally Posted by Arthurs View Post
I have a Skystream 3.7 mounted on an 80 foot tower. When I first installed it I could not get anything form the generator and a friend with experience said it was because of my grid connection which was a "Y" from the utility which is the typical three phase configuration. I was planning a solar and they said when I got the inverter running that the generator would run. I had to get a single phase grid from the utility to get the Xantrex to lock onto the grid but then the generator started working.

My problem now is that the generator ran about ten days then stopped with a good wind. It had been producing well during those ten days. My location has a steady wind most days.

When I look at the remote it says normal but zero Kwh since it is not turning. I climbed the tower and the blade can be turned easily by hand.

Does anyone have any ideas of what my problem could be. I have written to Skystream customer service by email three times and get no response. From reading the book it appears that the latching relay may need to be reset. Does anyone know what voltage needs to be applied to activate the coil on the latching relay.

Dave
__________________
3kW-Siemens SR100,2/SW4048,MX60, Kestrel220/65' tower, Discover AGM batteries
Reply With Quote
  #4  
Old February 18th, 2010, 21:43 PST
niel's Avatar
niel niel is offline
Super Moderator
 
Join Date: Jun 2003
Location: pittsburgh, pa
Posts: 4,882
Default Re: Skystream 3.7

what in the world do you consider perfect? a tower sitting perfectly level as you term it will have some small degree of sway in the wind. there is no perfect and if it is that difficult to turn the thing into the wind, i wouldn't want it.
why is it always the fault of the guy that owns it and not the fact that it is a poorly functioning albatross? what will the next excuse be for it, because it was a tuesday?
__________________
NIEL-N3GHX (not employed by naws)
Reply With Quote
  #5  
Old February 18th, 2010, 22:01 PST
BB. BB. is offline
Just some guy
 
Join Date: Mar 2006
Location: SF Bay Area (California)
Posts: 7,818
Default Re: Skystream 3.7

From what I have read elsewhere (if I recall correctly), the towers can change level at the top plate enough to cause problems just from differential heating/expansion cause by sunlight on the monopole towers.

Sort of the problem with a "down wind design" and no aerodynamic "tail"/vane.

-Bill
__________________
20x BP 4175 panels + Xantrex GT 3.0 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.
Reply With Quote
  #6  
Old February 19th, 2010, 7:21 PST
blackswan555 blackswan555 is offline
Solar Panda
 
Join Date: Nov 2008
Posts: 195
Default Re: Skystream 3.7

Quote:
When I look at the remote it says normal but zero Kwh since it is not turning. I climbed the tower and the blade can be turned easily by hand.
The blade can be turned easily by hand, But the wind is not turning it ?

Tim
Reply With Quote
  #7  
Old February 19th, 2010, 8:57 PST
russ russ is offline
Solar Superstar
 
Join Date: Oct 2009
Posts: 326
Default Re: Skystream 3.7

Not to mention about the only organization that ever tries to come close to perfect is NASA.

Any structural code has tolerances.
Reply With Quote
  #8  
Old February 19th, 2010, 10:28 PST
halfcrazy halfcrazy is online now
Solar Potentate
 
Join Date: Dec 2004
Posts: 511
Default Re: Skystream 3.7

That is a common problem with down wind turbine's If the tower top isn't perfectly level the turbine will tend to spin to the low spot. SWWP actually makes a rig you put on the top of the tower and make sure it is level.
__________________
MS-AE Magnum 120/240 vac inverter, MidNite E-Panel, 2 MidNite Classic's, Outback FM60, 790 ah Trojan L16 batteries, 2970 watts of pv. 10 foot wind turbine and no light bill for 7 years
Reply With Quote
  #9  
Old February 22nd, 2010, 19:26 PST
Watt Watt is offline
Registered Guest
 
Join Date: Dec 2009
Posts: 17
Default Re: Skystream 3.7

Quote:
Originally Posted by niel View Post
what in the world do you consider perfect? a tower sitting perfectly level as you term it will have some small degree of sway in the wind. there is no perfect and if it is that difficult to turn the thing into the wind, i wouldn't want it.
why is it always the fault of the guy that owns it and not the fact that it is a poorly functioning albatross? what will the next excuse be for it, because it was a tuesday?
AMEN to the man who describes it best.
Reply With Quote
  #10  
Old February 24th, 2010, 6:58 PST
BillF BillF is offline
Registered Guest
 
Join Date: May 2009
Posts: 39
Default Re: Skystream 3.7

Quote:
Originally Posted by BB. View Post
From what I have read elsewhere (if I recall correctly), the towers can change level at the top plate enough to cause problems just from differential heating/expansion cause by sunlight on the monopole towers.

Sort of the problem with a "down wind design" and no aerodynamic "tail"/vane.

-Bill
You're right. Monopole towers have a probelm with this although I'm not sure how far a tower would deviate. Probably related to color/thickness of steel etc.

Any downwind turbine regardless of make will have to have a plumb tower and level mounting flange. SWWP is providing the "Skylevel" to assist with this. Proven has added a vane of sorts to overcome directionality problems. The Illinois Northwind doesn't have anything to help guide it although that may come later with product developement.

Even traditional tailed turbines can be affected by less than plumb towers as the weight of the tail assembly will swing the turbine to the weighted side thus affecting low wind orientation.

It's just good practice to carefully align/plumb/level the tower that has a turbine regardless of brand or make mounted on it and regularly check for deviation.
__________________
3kW-Siemens SR100,2/SW4048,MX60, Kestrel220/65' tower, Discover AGM batteries
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Skystream - Down BassLaker Wind Power Generation 6 February 22nd, 2010 19:16 PST
Skystream Clone? BillF Wind Power Generation 9 July 29th, 2009 14:05 PDT
Skystream 5.0 Truth Squad Wind Power Generation 12 May 11th, 2009 16:51 PDT
Another Skystream problem Country Gale Wind Power Generation 2 July 27th, 2008 17:19 PDT