Default Re: Battery less vs. battery based grid tie

Hmm... If the Sunny Island "GT system" responds within a few seconds... Then it really needs the Sunny Island Inverter+Battery system to carry through the starting loads... Which only makes sense as the "true" GT / Utility Interactive systems apparently have a "fairly long" time constant (per a Solar Guppy post in another thread, probably to prevent oscillations between the inverter and utility power).

An Off-Grid inverter would need to respond within 1/2 cycle (1/120 Hz = 8.3 mSec) to be a "useful power source" for an off grid system.

-Bll
__________________
20x BP 4175 panels + Xantrex GT 3.0 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

Last edited by BB.; July 11th, 2010 at 15:20 PDT.
Reply With Quote
  #12  
Old July 11th, 2010, 13:40 PDT
stephendv stephendv is offline
Solar Superstar
 
Join Date: May 2009
Location: Barbastro, Spain
Posts: 292
Default Re: Battery less vs. battery based grid tie

Not sure if we're talking about the same response here, I meant the response to varying the GT output based on the loads when already operating in off-grid mode. And in this case the GT has to be a sunny boy.
E.g.: Grid is down, batteries fully charged, GT and AC loads and SI are all on the same AC bus. Frequency is now controlled by the SI. If the loads are less than the GT then the time it takes for the SI to increase the frequency and the GT to reduce it's output correspondingly is only a few seconds.

EDIT: Ah, I think I see what you mean now, yes the SI will have to carry the loads through until the GT can respond.

Last edited by stephendv; July 11th, 2010 at 13:52 PDT.
Reply With Quote
  #13  
Old July 12th, 2010, 6:56 PDT
Dave Sparks's Avatar
Dave Sparks Dave Sparks is online now
Solar Potentate
 
Join Date: Apr 2009
Location: California Sierra near Mariposa
Posts: 594
Default Re: Battery less vs. battery based grid tie

If you have to have two inverters it really make little sense for my "hypothetical" customer. I am thinking that with the modern slow start refrigerators someone would devise a way to avoid spoiling food and batteries.

I like the idea of no driving at night Bill, not sure about the tunnel part yet...
__________________
http://www.sierratel.com/offgridsolar/
"we go where the power lines don't"
Reply With Quote
  #14  
Old July 28th, 2010, 17:33 PDT
RCinFLA's Avatar
RCinFLA RCinFLA is online now
Solar Potentate
 
Join Date: May 2006
Location: Florida, USA
Posts: 552
Default Re: Battery less vs. battery based grid tie

One thing that came to mind....

Solar Maxima is coming 2011-2012. Some predictions are it will be worse since 1958.

Demand for power distribution transformers may go up.
Reply With Quote
  #15  
Old July 29th, 2010, 11:54 PDT
tallgirl tallgirl is offline
Solar Panda
 
Join Date: Jul 2009
Location: Austin, TX
Posts: 233
Default Re: Battery less vs. battery based grid tie

Quote:
Originally Posted by RCinFLA View Post
One thing that came to mind....

Solar Maxima is coming 2011-2012. Some predictions are it will be worse since 1958.

Demand for power distribution transformers may go up.
Huh? Which predictions, and which way "worse"?

Besides, the likelihood we reach Solar Max in 2011 or 2012 is close to nil. We still setting records for "boring". This cycle would have to get past the "Yawn" level of excitement first.
__________________
Julie in Texas

greenMonitor(tm) for OutBack Power Systems from greenHouse Computers. Now available on your phone, too.
Reply With Quote
  #16  
Old July 29th, 2010, 14:40 PDT
dwh's Avatar
dwh dwh is offline
Solar Stumblebum
 
Join Date: Mar 2009
Location: San Fernando Valley, Los Angeles, Ca.
Posts: 831
Default Re: Battery less vs. battery based grid tie

Actually, NASA and NOAA are predicting the peak of Cycle 24 in May 2013. It's not supposed to be a particularly high peak, but they think there is a good chance of a few pretty big flares.

http://www.swpc.noaa.gov/SolarCycle/SC24/index.html
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -7. The time now is 11:40 PDT.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Copyright 1997-2010 Northern Arizona Wind & Sun