    Default Re: Wellsee MPPT

    You can only parallel Charge Controllers on the output... For various reasons, you cannot parallel two chargers on the same solar array charging the same battery bank.

    Adding diodes on the array or at the battery bank will not help, and with the battery bank will mess-up the charging voltage readings by the charge controllers (diode drop) and may cause the controllers to not work at all (controllers usually need to sense battery voltage and use a small amount of power to even startup).

    -Bill
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

  2. #12
    Join Date
    Oct 2009
    Location
    Weatherford Texas
    Posts
    38

    Default Re: Wellsee MPPT

    I am feeding a 2nd array to the battery bank. I am trying to get 120amps into the battery bank.

  3. #13
    Join Date
    Mar 2006
    Location
    SF Bay Area (California)
    Posts
    16,889

    Default Re: Wellsee MPPT

    Two separate arrays, two solar charge controllers, both connected with short heavy leads directly to the same battery bank--Should work fine.

    -Bill
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

  4. #14
    Join Date
    Mar 2009
    Location
    Los Angeles, Ca.
    Posts
    1,332

    Default Re: Wellsee MPPT

    Quote Originally Posted by moorsb View Post
    I am feeding a 2nd array to the battery bank. I am trying to get 120amps into the battery bank.
    How full is the battery bank? Perhaps one unit has raised the voltage to the point where the second unit thinks the battery is charged.

    Test them separately when the battery is down a bit.

  5. #15
    Join Date
    Oct 2009
    Location
    Weatherford Texas
    Posts
    38

    Default Re: Wellsee MPPT

    I have added a TM2020 to the system. I am not sure at all if I have it programmed correctly. That is the worst manual and instruction for setup that I have ever seen. It is like someone translated the step by step and left out things like, why am I doing this what effect does this have on the system. To enter the mode where you enter the bank capacity I had to turn off loads to get its attention seemed like it was too busy calculating things to catch the keyboard strokes. At this point I the volt were set 14.3 amps 99 is that as high as it will go I have over 100a from pv.
    I will have to play with this before I believe any data. It shows the battery fully charged the MPPT is still charging. and the MPPT show the battery not fully charged. I am not sure what number to plug in for the bank capcity it say to enter half if you do not want to discharge them very much so I entered 600 amps

  6. #16
    Join Date
    Oct 2009
    Location
    Weatherford Texas
    Posts
    38

    Default Re: Wellsee MPPT

    They seem to be working. I have a 1.5 kva transformer on the output of the inverter. If I leave the inverter on over nite my tri metric tells me the battery is down to 85% full in the morning and it is full at night. I tried a 5 kva transformer on over nite and the battery is down to 50%
    I guess I should rewire the pump to 120 vac and kill the transformer.

  7. #17
    Join Date
    Oct 2009
    Location
    Weatherford Texas
    Posts
    38

    Default Re: Wellsee MPPT

    The TM 2020 looks like I need to reconfigure. It says it has met charge criteria yet it shows 10 amps going into the system with little load. The MPPT controllers one says the battery is full the other one says it is not so I guess just one is charging the bank once it gets to this level. I have rewired the pump to 120vac and taken out the transformers. I am setting up to run my xmas lights outside too. The lights are drawing 50 amps out of the battery. I have them on a timer for 4 hours. This morning the TM2020 showed down 210 amps. The solar panels were pumping 50 amps back in this morning and by 11:30 I was back at 100 percent according to TM2020 but I noticed 10 amps still be pumped into the bank with minimal load. So I guess I need to reprogram the TM2020?

  8. #18
    Join Date
    Sep 2007
    Location
    Fox, Arkansas
    Posts
    379

    Default Re: Wellsee MPPT

    I noticed 10 amps still be pumped into the bank with minimal load. So I guess I need to reprogram the TM2020?
    I haven't followed this thread closely, but depending on your battery bank, it could draw 2 to 10 amps just to float it. I have forklift batteries, 940 amp hours and it takes 2 to 3 amps to float.
    15 assorted solar panels 1800 watts
    MX 60 charge controller
    940 amp hour 2 X 6-100-13 DEKA batterys
    TriMetric battery monitor
    SW4024 inverter
    Basic Stamp computer to control SW4024 from MX60

    MikeO

  9. #19
    Join Date
    Jan 2011
    Location
    Off Grid Gulching it in NM
    Posts
    10

    Default Re: Wellsee MPPT

    Hi Gang.

    I have one of the 24Vin 12Vout, 20 AMP ones, purchased direct from Welsee in China.

    First, the good news: Service was good, only took a week to get here.

    Had it in service for two days now, feeding a 400AH bank off of two Kyocera 205 watt 24V panels in parallel.

    Just using it to keep the batteries that run my lights and furnace blower in the RV topped off.

    It charges the batteries OK, but it is NOT MPPT (at least as far as my limited understanding of the concept goes), just as earlier posters have surmised. Amps out is slightly less than amps in, but since the voltage is just about halved, I'm losing about half the wattage that the panels put out.

    Here is a photo of two Watts Up meters showing what is going into and out of the Welsee controller. The top meter shows what is coming off the solar panel, the bottom shows what is going into the battery bank;

    (I have photos of the inside of the controller as well, if anyone is interested.)
    Attached Images Attached Images  
    Last edited by Gulch; January 21st, 2011 at 23:00 PST. Reason: clarification

  10. #20
    Join Date
    Jan 2011
    Location
    Off Grid Gulching it in NM
    Posts
    10

    Default Re: Wellsee MPPT

    By the way, even when the batteries are down to 12.0 volts the controller still puts out a fraction less than 1/2 the watts that are going into it. The batteries haven't gone below 12.0V since I got the controller, so I can't say definitively that there won't be a better efficiency throughput if the batteries are deeply discharged.

Similar Threads

  1. Combining MPPT and Non-MPPT Charge Controllers
    By sepsolman411 in forum Solar Beginners Corner
    Replies: 6
    Last Post: July 29th, 2012, 0:27 PDT
  2. Morningstar MPPT Charge Controller Setup Question SS-MPPT-15L
    By chetwynd in forum Off Grid Solar & Battery Systems
    Replies: 7
    Last Post: February 22nd, 2012, 20:39 PST
  3. Morningstar MPPT Charge Controller Setup Question SS-MPPT-15L
    By chetwynd in forum Solar Product Reviews & Opinions
    Replies: 0
    Last Post: February 22nd, 2012, 13:51 PST
  4. Blue Sky patented MPPT vs other MPPT controllers?
    By _OS_ in forum Advanced Solar Electric Technical Forum
    Replies: 11
    Last Post: February 3rd, 2009, 15:04 PST

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •