    Default Inverter generator AC plug Neutral

    Does anybody have a schematic or direct knowledge of the inverter output design on inverter generators.

    I have a Yamaha EF3000sei. As an EE, I expect the pulse width modulated inverter bridge does not allow for direct connection of neutral side of 120 vac plug to ground as is required for SW series inverters connected to house wiring.

    The service manual shows testing of the three phase rectified alternator at full RPM to produce 200 to 240 vdc. This would be inline with a full wave push-pull bridge FET chopper, meaning neutral is not groundable.

    It is possible if the neutral is grounded the isolated power module will float up and down along with the 60 Hz output. I am concerned about possible effects of stray capacitance from power module/alternator coil to ground if this grounding of the neutral side of plug is attempted. (similar problem the small stand-alone inverters have). Other likely issue is perhaps bypassing half of a ground center tapped inverter bridge output filter. Yamaha's official answer is the inverter generator can not be transfer switch connected to house electrical panel and is only intended for direct plug-in connection to individual appliances.

    To be safe I am putting the Yamaha output through an isolation transformer prior to AC2 input on SW inverter. I can then safely tie SW neutral to breaker box neutral which is ulimately ground bonded at box.

    To me, all this extra work/expense is worth the benefit of the very quiet generator.

  2. #2

    Default Re: Inverter generator AC plug Neutral

    Generators as a rule already have their neutral bonded to the chassis frame. I have not heard of a problem connecting an inverter/generator to an inverter/charger. They workk great. I've talked to probably 100 people that use this type of generator.

  3. #3
    Join Date
    May 2006
    Location
    Florida, USA
    Posts
    1,232

    Default Re: Inverter generator AC plug Neutral

    Generators as a rule, are not inverter generators. With a scope I see equal and opposite sinewave at half the full output from neutral to ground and hot to ground.



  4. #4

    Default Re: Inverter generator AC plug Neutral

    I use a Honda EU2000i with my Outback VFX 2812 and it works perfectly, no modifications necessary.
    Larry
    Off Grid in Bahia de Los Angeles, Baja Norte , Mexico. 2 stacked Outback VFX2812 inverters, 12 Evergreen 190w PV (2.28 kw), 2 Homemade solar trackers, FM 80 and MX 60 charge controllers, E-meter(same as Link 10) battery monitor system, 6-2v Enersys DDM AGM 125-33 batteries@2000amp hours, Kubota 6.5kw diesel gen. Outback X-240 transformer.

Similar Threads

  1. MSW inverter Voltage between Neutral and ground
    By deltarat in forum Off Grid Solar & Battery Systems
    Replies: 5
    Last Post: February 27th, 2012, 20:45 PST
  2. Neutral & Ground Inverter Wiring
    By david3 in forum Solar Beginners Corner
    Replies: 45
    Last Post: October 15th, 2011, 7:22 PDT
  3. neutral bonding issues SS 300 inverter
    By bobdog in forum Off Grid Solar & Battery Systems
    Replies: 18
    Last Post: September 19th, 2010, 8:22 PDT
  4. Where to tie neutral to ground?
    By Bigwooo in forum General Solar Power Topics
    Replies: 2
    Last Post: August 11th, 2008, 19:33 PDT
  5. Comon Neutral
    By planetharman in forum Advanced Solar Electric Technical Forum
    Replies: 10
    Last Post: August 6th, 2007, 22:21 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •