Thread: service upgrade required?

  1. #11
    Join Date
    Jun 2003
    Location
    pittsburgh, pa
    Posts
    9,234

    Default Re: service upgrade required?

    ok so add about 12.5amps to the 100amps and i still see no need to go to a 200amp panel let alone a 150amp panel. a 100amp panel can easilly go 125amps and 112.5amps is still below that. let's put the speculation aside and wait to hear what the explanation is.
    voltage drop calculator http://www.wind-sun.com/ForumVB/showthread.php?t=29


    NIEL (not employed by naws)

  2. #12

    Exclamation Re: service upgrade required?

    a 100amp panel can easilly go 125amps
    Not according to NEC 690.64(B)(2). Here is what the section says for commercial applications:

    The sum of the ampere ratings of overcurrent devices in circuits supplying power to a busbar or conductor shall not exceed the rating of the busbar or conductor.
    If a commercial installation panel / busbar rated at 100 A, and it’s supplied from the grid via a 100 A breaker, then no other power sources (i.e., PV and inverter) can be connected to the panel as a power source.

    The reference NEC article includes a 120% exception for residential applications. For example, if a 100 A panel / busbar is supplied from the grid via a 100 A breaker, then another power source can be connected via a 20 A breaker.

    So, the NEC limit would be 120 A on a 100 A panel / busbar for residential applications.

    HTH,
    Jim / crewzer
    120618: System off-line for a while...

  3. #13

    Default Re: service upgrade required?

    This is a residential application. There is plenty of room on a new (2005) subpanel. Or some of the existing load can be moved from the main panel to the subpanel if that matters.

    Will inquire tomorrow.

  4. #14

    Default Re: service upgrade required?

    After further review, it seems the upgrade is neither necessary nor required by code. Thanks for the insights.

  5. #15
    Join Date
    Jun 2003
    Location
    pittsburgh, pa
    Posts
    9,234

    Default Re: service upgrade required?

    could you elaborate on who said what?
    voltage drop calculator http://www.wind-sun.com/ForumVB/showthread.php?t=29


    NIEL (not employed by naws)

  6. #16

    Default Re: service upgrade required?

    The installer who said that an upgrade would be required misspoke. An upgrade is not necessary. (Technically, I think he was looking at the job site pics and/or notes of someone else's house, but was writing my proposal. He went back to the pics/notes of my job and saw that all was indeed well.)

  7. #17
    Join Date
    Jun 2003
    Location
    pittsburgh, pa
    Posts
    9,234

    Default Re: service upgrade required?

    or, in speculation, maybe he was trying to get away with something. good news for you and i thought as much.
    voltage drop calculator http://www.wind-sun.com/ForumVB/showthread.php?t=29


    NIEL (not employed by naws)

  8. #18

    Default Re: service upgrade required?

    This guy is totally above board. Excellent reputation, earned the old-fashioned way, and assiduously maintained. I'm a skeptic in general, and can say this was an honest mistake. Ever have two or three Word documents open at once? Save one file over another? Paste a bit of semi-custom boilerplate into a cover letter and forget to modify? That's what this was.

    (He would also not have profited from this, as he doesn't do underground service work, nor does his regular electric sub, so he would have to have found a suitable sub.)

    Some people are actually still honest.
    Last edited by xiphias; April 1st, 2008 at 18:39 PDT.

  9. #19
    Join Date
    Jun 2003
    Location
    pittsburgh, pa
    Posts
    9,234

    Default Re: service upgrade required?

    honesty in this day and age now that's a rarity. you going to have him do the work?
    voltage drop calculator http://www.wind-sun.com/ForumVB/showthread.php?t=29


    NIEL (not employed by naws)

  10. #20

    Default Re: service upgrade required?

    still looking at the household economics. might start with SDHW and add PV later as resources permit.

    This has been a useful and informative thread, and site. Thanks.

Similar Threads

  1. Is a Neutral Required Here?
    By Fronius in forum PV Installers Forum - NEC, Wiring, Installation
    Replies: 6
    Last Post: February 6th, 2012, 9:08 PST
  2. Thread Setting Help Required
    By REPO in forum Solar Forum News and Announcements
    Replies: 4
    Last Post: May 10th, 2011, 10:14 PDT
  3. Service Panel Upgrade Required?
    By solemio in forum Solar Beginners Corner
    Replies: 31
    Last Post: September 4th, 2009, 12:23 PDT
  4. Service panel upgrade or sub-panel
    By newenergy in forum Advanced Solar Electric Technical Forum
    Replies: 3
    Last Post: April 19th, 2008, 9:23 PDT
  5. Using panel that is smaller than required
    By rngd in forum General Solar Power Topics
    Replies: 6
    Last Post: January 11th, 2008, 8:18 PST

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •