Page 1 of 2 12 LastLast
Results 1 to 10 of 18

Thread: Need advise

  1. #1

    Question Need advise

    I would like to install a 4k solar system with grid interactive inverter. Facts on inverters are not clear, I will use 99% grid tie but would like a battery back up for outages. Which inverter will allow me to operate on grid only with or without battery's? Also I would like to be able to switch off the system and not see any difference in powering the house from the grid. So far I have been looking at Outback and Xantrex, Xantrex looks like the one I need but I'm not clear on how they both operate.
    Thanks

  2. #2

    Default Re: Need advise

    Welcome to the forum.

    "Grid Interactive" can mean a lot of things, so let's look at the three basic inverters and how they can interact with the grid.

    1). straight grid-tie: solar panels go directly to the inverter which then backfeeds the household/utility with whatever power it can muster from the panels. No back-up ability; grid goes down, you have no power.

    2). off-grid used for back-up: utility and/or panels keep batteries charged. Utility feeds loads when available, inverter feeds loads when the grid goes down. No selling of surplus power to the grid.

    3). hybrid system: panels keep batteries charged, surplus power production is sold to the utility. If the grid goes down inverter supplies back-up power from the batteries.

    All those will utilize grid power for the loads primarily, with the exception that if you have surplus power it will either be sold back to the utility or lost.

    Both the Outback Radian or Xantrex XW systems are of the hybrid variety. They can supply power from the batteries when the grid goes down, or sell surplus panel production when it is up.

    I also have to mention that if your goal is back-up power for occasional, short outages you are better off buying a generator. Solar power systems, especially battery-based, are expensive. As back-up power it is usually not a good choice unless the outages are frequent, long-lasting, or involve critical loads that must be maintained.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  3. #3

    Default Re: Need advise

    So far the information I see is that the outback inverter won't run w/o batteries, the Xantrex will. This has to be a system that anyone can operate, like my wife if I was not home. My ultimate goal is to sell power and be a little more self reliant. The battery backup makes sense to add at the beginning.
    Looks like Outback runs thru the battery's all the time. If I lost one battery out of 4 (48v) then my transferred loads would all go down. Xantrex looks like it will run on its own w/o the battery's. Is there a better inverter that I haven't researched? I to new at this to risk tons of money and find out that I missed something.

  4. #4

    Default Re: Need advise

    The hybrid inverters need to have batteries all the time. They just don't need so many of them as a straight off-grid system does. Plus, any loads you want to be battery backed, run on the inverter all the time meaning you can't switch off the inverter system and just be on the grid without rewiring these loads. Most setups do have a bypass switch for doing this however. My advice is to do a straight grid-tied system as it is more efficient, way more reliable and more cost effective - and just get a generator for those infrequent outages. Of course if you have lots of money to spend, give me a call.
    2.7kW Trina/Xantrex GT, 2.7kW Trina/SolarEdge, 2kW CSI/SMA GT, Solar well pump on 6, 25yr old Holeck 48W modules. Toyota SR5 converted to 108V EV. Prius w/Enginer PHEV conversion. BSEE, C11-residential, NABCEP, SunnyPro >450kW installed
    "Faced with the choice between changing one's mind and proving that there is no need to do so, almost everyone gets busy on the proof." - John Kenneth Galbraith

  5. #5
    Join Date
    Apr 2010
    Location
    Austin, TX, USA
    Posts
    1,526

    Default Re: Need advise

    Quote Originally Posted by kenr047 View Post
    I would like to install a 4k solar system with grid interactive inverter. Facts on inverters are not clear, I will use 99% grid tie but would like a battery back up for outages. Which inverter will allow me to operate on grid only with or without battery's? Also I would like to be able to switch off the system and not see any difference in powering the house from the grid. So far I have been looking at Outback and Xantrex, Xantrex looks like the one I need but I'm not clear on how they both operate.
    Thanks
    You cannot run AC loads off grid without batteries no matter what inverter you buy, if that is what you are asking.

  6. #6

    Default Re: Need advise

    Quote Originally Posted by kenr047 View Post
    So far the information I see is that the outback inverter won't run w/o batteries, the Xantrex will. This has to be a system that anyone can operate, like my wife if I was not home. My ultimate goal is to sell power and be a little more self reliant. The battery backup makes sense to add at the beginning.
    Looks like Outback runs thru the battery's all the time. If I lost one battery out of 4 (48v) then my transferred loads would all go down. Xantrex looks like it will run on its own w/o the battery's. Is there a better inverter that I haven't researched? I to new at this to risk tons of money and find out that I missed something.
    No: the Outback Radian and Xantrex XW inverters (as well as any other hybrid inverter such as the SMA Sunny Island) need batteries all the time or else they do not work.

    I bring up the SMA because they also make straight grid-tie inverters (Sunny Boy) which can be coupled to the Sunny Island in a very manageable way. You could install a Sunny Boy GT system now and add the Sunny Island later for battery-based back-up.

    But as has been pointed out, no batteries = no back-up power.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  7. #7
    Join Date
    Jul 2012
    Location
    NW WA
    Posts
    327

    Default Re: Need advise

    The Outback GVFX3648 is a "grid interactive" inverter that is large enough to support most normal households and would work well with a 4kw array. It's much less expensive than the Outback Radian inverters, Xantrex XW series, or SMA Sunny Island.

    Unlike those however, when used alone - one GVFX will not supply 240 VAC loads without the use of an autotransformer. So - as always - it depends on what loads you are trying to supply/back up.

    It does, of course require batteries!
    Array 1: Sanyo HIT225 X 8 on Wattsun tracker. Array 2: Evergreen ES-E-225 X 12 on shed roof. Midnite e-panel with Outback GVFX3648, FNDC and Classic 150 X 2. 436 AH AGMs. Honda eu2000i X 2. Meanwell PB-1000-48.

  8. #8

    Default Re: Need advise

    I'm not asking the right questions based on the answers i"m getting.
    Will Xantrex still feed the grid (only the grid) with out batteries? Will any hybrid inverter?

  9. #9

    Default Re: Need advise

    Quote Originally Posted by kenr047 View Post
    I'm not asking the right questions based on the answers i"m getting.
    Will Xantrex still feed the grid (only the grid) with out batteries? Will any hybrid inverter?
    No hybrid inverter will work without batteries.
    The only inverter that will work without batteries is a Grid Tied Inverter.

    EDIT: You can connect a Grid Tied inverter to some battery based inverters like the Xantrex XW or SMA sunny Island.
    2.8kW Yingli PV, 5kW SMA Sunny Island 5048, 900Ah 48V Forklift battery, 5kW Petteroid Indian diesel generator

  10. #10
    Join Date
    Mar 2006
    Location
    SF Bay Area (California)
    Posts
    16,814

    Default Re: Need advise

    Xantrex has Grid Tied, Hybrid, and Off Grid inverters... So, it can get a bit confusing. It is the Xantrex XW Hybrid inverter that we are discussing here (and other brands).

    Hybrid inverters are really using the Grid/Utility power as a "dump load". When the batteries are "full", any excess power is sent out to the grid.

    You can setup a GT inverter to "back feed" some TSW type off grid inverters and actually recharge the battery bank (some Off Grid inverters are actually bi-directional regarding AC/DC power... The GT inverter can push current back through an Off Grid inverter and recharge the battery bank. The issue is how to control the charging of the battery bank. Normal Off Grid Inverters (when "back fed" power from a GT Inverter) do not have any way of stopping the recharging of the battery bank--so you either have to setup a dump load and/or controller to turn off the GT inverter when the battery bank is full.

    The Xantrex XW, and (I think) some Magnum inverters can shift the 60 Hz frequency to (for example) 62Hz when the battery is full. That will "knock" the GT inverter off line until the frequency is restored back to 60Hz.

    SMA's Sunny Island series is designed to vary/throttle the GT inverter the farther it gets from 60 Hz (it is actually quite smart and will not mess up your AC powered clocks as it keep track of how far the frequency has drifted).

    There is no "cheap way" of doing this. Basically, you are removing the standard MPPT type battery charger and replacing it with a GT Inverter. There are a few advantages (GT inverters are less expansive and can send high voltage power longer distances than the "standard" MPPT type battery chargers).

    -Bill
    Last edited by BB.; August 21st, 2012 at 7:30 PDT.
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

Similar Threads

  1. Looking for advise/help on my system
    By hackman22 in forum Off Grid Solar & Battery Systems
    Replies: 21
    Last Post: September 16th, 2012, 17:28 PDT
  2. Battery advise.
    By basewindow in forum Off Grid Solar & Battery Systems
    Replies: 20
    Last Post: September 10th, 2012, 8:48 PDT
  3. Me the mega newbie - please advise!
    By spydox in forum Solar Beginners Corner
    Replies: 8
    Last Post: April 3rd, 2012, 17:47 PDT
  4. Need some advise
    By Jim45D in forum General Solar Power Topics
    Replies: 8
    Last Post: January 22nd, 2012, 6:28 PST
  5. Should I Parallel or Series? Please advise.
    By drew4justice in forum Solar Beginners Corner
    Replies: 3
    Last Post: September 8th, 2011, 7:37 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •