Re: house ground question..

Originally Posted by
lamplight
Hi
i recently discovered our house ground (grid connected AC) wasnt working.. its connected to a copper water pipe about 5' below ground level through our field stone foundation.. it had corrodoed completely off... this morning i got a new zinc plated ground clamp, sanded the pipe to expose some shiny copper and reconnected it.
There is a large part of your problem! A zinc coated ground clamp is meant to be used on galvanized water pipes. For use on a copper rod or pipe you need a brass or bronze ground clamp.
Electrolytic (galvanic) corrosion between the zinc and copper will eat away at all points where the two touch. It will be strongest if they get wet or exposed to high humidity, but that is not necessary for damage to happen.
Last edited by inetdog; August 13th, 2012 at 13:57 PDT.