    Default Picking a generator

    I am struggling with the decision of choosing a generator for my soon to be installed Off-Grid system.

    Here is the system:
    The inverter/ battery system consists of:
    1) 1- Outback VFX 3648 inverter
    2) 1- Midnite 175 STS-L E-panel with circuit breakers for the inverter, charge controller and TM2020
    3) 1- Outback Mate inverter programming module
    4) 1- Set of 4/0 x 10' UL listed inverter battery cables
    5) 1- Outback FNDC battery monitor
    6) 16- Trojan L16-RE series 370 amp hour, 6 volt deep cycle batteries (740 amp hours @ 48VDC / 35,520 kWhrs AC)
    7) 16- 2/0 x 12" battery interconnect cables
    8) 1- 300 volt AC SPD surge arrestor
    The PV system consists of:
    1) 16- 255 watt PV modules (established name brand, to be determined by availability)
    2) 2- DP&W 8-module, adjustable tilt pole top mounts (4-6 week lead time from factory)
    3) 2- 6" x 21' schedule 80 pipes for array mounts (non-galvanized)
    4) 1- Classic 200 charge controller
    5) 1- Midnite MNPV12-250 combiner box (for 6 sub arrays)
    6) 4- Midnite MNEPV15-300 combiner breakers, 300 volt rated
    7) 1- 300 volt DC SPD surge arrestor

    First I'm not sure how to determine the correct size (i.e watts/A output needed). Answering the first question could make the type/brand question easier. I am considering an Ecogen from Generac for a couple reasons: 1, Made for off grid (so they say) and I am joining a group where I can get propane for a reasonable price. But I will have to have a good size LP tank installed to feed the generator, HW heater, and stove.Price is ~$3500+ the $1500 install + LP tank. On the other hand I was looking at a 7Kw Genset (Powered by Honda) to both charge the system and move around the farm and to use in my small wood shop as needed. Obvious disadvantage (to me) gas is expensive and I will need to keep more on hand, louder than the Ecogen, but the price is ~1K. If I got the Ecogen I would still need to buy a portable sometime for the reasons stated above but I may choose a smaller sized. I currently have a Honda2000i but it can't run my Radial arm saw our my smallish compressor.

    Any suggestions on 1)What size and 2) which way to go (LP,Gas)?

    Thanks
    McD
    Last edited by Cariboocoot; August 1st, 2012 at 7:01 PDT.

  2. #2

    Default Re: Picking a generator

    Your generator needs to be able to supply two things: enough current to charge the batteries at maximum rate and enough power above that to handle the loads that will be running at the same time. The more loads you can control (turn off) the smaller gen you can use and the less fuel.

    So you are looking at providing 74 Amps @ 48 Volts or 3552 Watts, plus the charger efficiency compensation (about 90%) or up to 4kW just to charge the batteries if they are seriously depleted. Your Honda 2000 isn't going to do this. Add some "load overhead" and you are looking at at least a 5kW genset.

    Which fuel? Well which is cheapest for you? You ave to have some numbers on the fuel efficiency of the generator, which can be hard to come by. Then you can compare the kW hours it produces to the amount of fuel it uses and how much that fuel will cost and get a $ per kW hour figure. It may also be better to use a more expensive fuel if that is more convenient. LPG costs less but is less efficient, however it stores well and you'd already have a big supply on hand for the appliances. You don't have to pour it from can to tank with a permanent install. Not fun in NY Winters.

    Hondas are extremely good quality equipment. I can't say the Generac stuff has all had the same sort of reviews.
    There are numerous threads on the forum about generators and people's satisfaction with them. Unfortunately I'm on the "wrong" computer and haven't got my sixteen million bookmarks handy.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  3. #3
    Join Date
    Mar 2006
    Location
    SF Bay Area (California)
    Posts
    16,845

    Default Re: Picking a generator

    Remember too that propane has less energy per gallon vs gasoline (and diesel is more energy per gallon vs gasoline). Around 84,000 to 93,000 BTU per gallon vs 111,000 to 114,000 BTU per gallon for gasoline. So, while LPG may cost less per gallon, a genset will use more fuel to make up for the lower energy content (although, if no road taxes, it LPG may still cost way less).

    The Ecogen seems to have some folks here that like them. You can use Google to search the forum. Type "ecogen site:wind-sun.com" (without the "") (here is a google search link) and you should get a lot of hits on various threads.

    It probably would not hurt to have a diversity of fuel and a backup genset if you have critical needs (ability to run the tools during if the first generator fails, ability to get backup fuel supply--i.e., can get gasoline but no propane delivery, etc.).

    That said, propane is going to be the easiest to store (I keep 20 gallons of emergency gas, recycle to the car every year and refill with stabilizer). But watch the tank costs. Somebody said a few years ago that their propane supplier decided to charge a tank rental fee, then jacked the price up over the years until now people are considering dropping propane service.

    Also, most gensets at 50% or less power will run about 50% fuel flow (Gallons per hour). So--I am a big fan of "not too big" of genset. Running a 7kW genset is going to use (probably) over a 1 GPH for propane at 3.5 kW or less loads. The Honda eu2000 will use ~0.25 GPH for a 1,500 watt load (down to 9+ hours per 1.1 gallons of gas to supply 400 watts average).

    So, you may end up with two or more gensets to match the loads needing to be powered at the time for optimum fuel economy. I would suggest a Amp/Watt/kWH meter on your generator circuit(s) so you can monitor the power usage and even calculate the kWH/Gallon fuel usage.

    -Bill
    Last edited by BB.; August 1st, 2012 at 8:32 PDT.
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

  4. #4

    Default Re: Picking a generator

    I have not used one, but Honda does have some larger inverter-generators like this 4500 Watt unit: http://powerequipment.honda.ca/gener...5000isc2/specs

    Contrary to what some people may say, the efficiency of output is not the only consideration in a generator. In the case of the inverter types the over-all fuel consumption is less than a conventional generator even the the output per quantity of fuel consumed may not be as good. They shine when the loads reduce, which is an inevitable state when recharging batteries (you only need the maximum power at the start).

    Since others have converted their smaller Hondas to propane it should be possible to do the same with the larger units and get the best of both worlds.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  5. #5
    Join Date
    Jun 2007
    Location
    Center of Nowhere, NOR CAL
    Posts
    1,253

    Default Re: Picking a generator

    For portable use, LP (Propane) powered gensets are a bit of a pain. So as noted by BB Bill, having several gensets of differing sizes and fuel sources is probably going to be very convenient. Would expect that one would find at least one gasoline-fueled genset very convenient. They do need to have fuel poured into their tanks, unless fueled from a nurse tank. But if you have gasoline fueled vehicles on the farm, it is nice to have one or more gasoline fueled gensets.

    Honda brand gensets are very solid, and are very conservatively rated. (the Honda brand generators I've looked at have a Surge rating of 20 or on some, 30 minutes -- much better than any of the inexpensive generators). Have used Honda brand genssets here, of varying sizes, and all of them have been very reliable and trouble free. We do use an Inverter genset, similar to the one linked by Marc, installed as the backup genset to the main Diesel, and it is quiet and fuel stingy, but needs fuel poured into its tank.

    Regarding the Generac Ecogen 6500, or 6.5 (forget), some here do use them. One member reported a motor siezure on one at abaout 41 hours, but was being replaced under warranty. Elsewhere, there have been reports of users having diffficulty doing the Field Upgrade from 120 VAC to 240 VAC output. The issue was incorrect output voltage after the upgrade. Something about a new Control board or similar being needed. It is quite possible this has been resolved by Generac by now.

    Some extended discussion of the Generac Ecogen here:
    http://www.outbackpower.com/forum/vi...hp?f=17&t=4591

    There is no simple answer to the question of just which genset, or even fuel source for gensets. Many trade-offs. Good Luck, Vic
    Last edited by Vic; August 1st, 2012 at 9:38 PDT. Reason: Added Link, TYOP, Make certain mispellings intact!
    Off-Grid, Sys1: 1280 AH 48 V bat, 3.150 KW STC PV, MX-60, Xantrex Stacked SW+ 5548s; EU6500isa, 21KW Kubota diesel gens, misc Honda Eu gens
    Sys2: 1280 AH 48 V 4KS25 Surrettes, 5.88 KW STC, Two Classic 150s, MN SPDs, Stacked X SW+ 5548s; Kohler 18 KW LP, EU 3000isa gens, HB DC Charger, Midnite Breakers/boxes. Thanks for this great Forum!

  6. #6
    Join Date
    May 2012
    Location
    Upstate NY, Finger Lakes
    Posts
    100

    Default Re: Picking a generator

    I understand that the brand and fuel choice is never a clear cut choice. I have to decide which one but it sounds like I need one in the 5-7Kw to get the amperage I need for the 740Ah battery bank.

  7. #7

    Default Re: Picking a generator

    Can someone explain this exchange to me. I'm trying to understand a similar issue and now this has me confused.

    Rngr275 wrote: 16- Trojan L16-RE series 370 amp hour, 6 volt deep cycle batteries (740 amp hours @ 48VDC / 35,520 kWhrs AC)

    Cariboocoot replied: So you are looking at providing 74 Amps @ 48 Volts or 3552 Watts

  8. #8
    Join Date
    Nov 2011
    Location
    central Vermont
    Posts
    1,163

    Default Re: Picking a generator

    Quote Originally Posted by Toby View Post
    Can someone explain this exchange to me. I'm trying to understand a similar issue and now this has me confused.

    Rngr275 wrote: 16- Trojan L16-RE series 370 amp hour, 6 volt deep cycle batteries (740 amp hours @ 48VDC / 35,520 kWhrs AC)

    Cariboocoot replied: So you are looking at providing 74 Amps @ 48 Volts or 3552 Watts
    Recommended to charge batteries at 10% of their amphour rating. --vtMaps
    4 x 235w Samsung, Outback fm60 & vfx3524 & mate, Midnite E-panel, four Interstate L16, Trimetric monitor, Honda eu2000

  9. #9

    Default Re: Picking a generator

    Quote Originally Posted by Toby View Post
    Can someone explain this exchange to me. I'm trying to understand a similar issue and now this has me confused.

    Rngr275 wrote: 16- Trojan L16-RE series 370 amp hour, 6 volt deep cycle batteries (740 amp hours @ 48VDC / 35,520 kWhrs AC)

    Cariboocoot replied: So you are looking at providing 74 Amps @ 48 Volts or 3552 Watts
    8 batteries in series gives 48V and then in parallel with the next 8 gives 740AH. At a 10% charge rate you would need 74A. Add effeciency and you'll need about a 4-5K gen and a 48V charger.

  10. #10

    Default Re: Picking a generator

    Ok, I see it now. I could not figure out why the difference between 740 and 74 other than the missing zero.

    Is 10% used for charging by solar panels too or only for electrically powered chargers?

Similar Threads

  1. Wiring a generator to a Grundfos IO 101 Generator Box
    By eagle1tx in forum Solar Water Pumping
    Replies: 2
    Last Post: May 26th, 2011, 5:43 PDT
  2. First post need help picking solar panals
    By Alaska Lance in forum Solar Beginners Corner
    Replies: 14
    Last Post: September 14th, 2010, 19:38 PDT
  3. Xantrex XW, Generator not being qualified until load applied to generator
    By Les Nagy in forum Off Grid Solar & Battery Systems
    Replies: 14
    Last Post: July 27th, 2010, 17:04 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •