rollandelliott
"It(vertical stacks) can be beneficial by reducing recirculation, particularly in installations using multiple condensing units. "
I have 2 outside compressors One for lower floor and other one for upper floor of a big house. They are about six feet apart. I could make a duct work out of some sheet metal, wonder if it woudl be beneficial?
You can get a quick idea of whether this even needs further investigation by measuring the air temperature around the upper condensor to see if it is being heated by the lower condensor. A difference of a degree or two probably will not justify the extra work, but at least you will have something to go on. The other thing to look at, of course, is whether the temp of the air being pulled into the lower unit is higher than the air temp 6 or more feet away from it. (Be sure not to be confused by reading with the thermometer in direct sunlight.)