    Hi Cariboocoot,

    Great advice there.

    I didn't think about having to charge/boost it with a 24v charger - incorporated with the invertor.
    Will check some out today if i get time.

    Those premade buggy cables look good for equalising, but i wont buy anything unitl i get the system up and running.

    I'll do some hunting for a invertor / booster.

    Cheers,
    Alan.

  2. #22

    Default Re: About to buy new Batteries - not sure if my set up is correct to start with

    It occurs to me we may be talking at cross purposes here.

    "Equalization" is a charging process where battery Voltage is raised above normal to bring the specific gravity of cells in line with one another; equal. Wire gauge does not matter here; if it's large enough to handle the high current of the Bulk stage it will be fine for the rest.

    I think you may be thinking of the benefit of pre-made cables of the same length being used to connect batteries so that the current is shared equally between two (or more) parallel connections. In this case it is essential that all parallel cables be the same gauge and length; equal.

    I hope that clears that up.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  3. #23
    Join Date
    Jul 2012
    Location
    Gold Coast Australia
    Posts
    14

    Default Re: About to buy new Batteries - not sure if my set up is correct to start with

    Quote Originally Posted by Cariboocoot View Post
    It occurs to me we may be talking at cross purposes here.

    "Equalization" is a charging process where battery Voltage is raised above normal to bring the specific gravity of cells in line with one another; equal. Wire gauge does not matter here; if it's large enough to handle the high current of the Bulk stage it will be fine for the rest.
    Yeah that's ok. I understand the difference. That little much i know....


    Quote Originally Posted by Cariboocoot View Post
    I think you may be thinking of the benefit of pre-made cables of the same length being used to connect batteries so that the current is shared equally between two (or more) parallel connections. In this case it is essential that all parallel cables be the same gauge and length; equal.

    I hope that clears that up.
    I was thinking of using my existing 'thick' cables and using those others to 'equalise' the 'rest'.


    As for the Controller and Charger with some of the brands you have mentioned is now a big problem with the price. There isn't any way we can afford those sorts of prices. Of course i am guilty - as the question of the guy bying a Rolls Royce: If you have to ask how much,, etc.

    Just thinking about the 12v to 24v conversion and how the panels are wired up on the roof. Will do anotherbasic diagram as to what i mean...

    Have a good night guys..

    Cheers.
    Alan.

  4. #24
    Join Date
    Jun 2007
    Location
    Williams Lake, BC
    Posts
    2,071

    Default Re: About to buy new Batteries - not sure if my set up is correct to start with

    there is another way to supply your 12 v loads, if they are low enough, and that is to get a reasonably priced 12V pwm charge controller and have it charge 1 -12 v battery, that may keep SWMBO happy in the switch over to all 24v...
    100% Off Grid @ 51* 46' N lat 124* 44' W long

    New House system: MX-60 w RTS, 2 - 120 W 12v PVs, 2 - C&D AT-15P AGM 24V 950Ah, Cotek ST1500W inverter, TBS 30a-24v Omni-charger, Honda Eu3000is, CL 150 coming out of a box, coming - 2 arrays @ 2240W

    Guest cabin system: 3 - 70W panels to SB 2000e CC, with 2 - 100 ah 12v SAFT wet NiCd's , 600W TSW Inverter

    Mothballed :Absolyte AGM 1055 Ah 12 v battery, XBM w/ Palm Vx data recorder, 3500 W Mitsubishi genset, TC40 (12V) charger ...

  5. #25
    Join Date
    Jul 2012
    Location
    Gold Coast Australia
    Posts
    14

    Default Re: About to buy new Batteries - not sure if my set up is correct to start with

    Hi all,
    Been away for a bit. And we have saved some money to go ahead with the 24volt setup.

    I have ordered 8 T105's RE's.

    And i just wanted to know how i have to change the cabling system to get 24v into the PL60 regulator.

    This is the roof setup:
    http://i202.photobucket.com/albums/a...ps207a3b65.jpg

    There are 5 panels (in a bank), and wired to be give out 12v.
    There are 4 banks (sending 4 feeds of 12volts to the regulator).
    There is approx a 4-6mtr run to the edge of the roof. And then a further 7-8mtr run to the Regulator. These runs are one continuous cable.

    So a real stupid question, but i have to ask:
    As a bank of panels is giving out 12v, is it ok to make two (out of the four feeds), to join two of them in series (giving 24volts) at the input of the bus bars?

    So in effect i will make the 4 feeds join into two 24v feeds at the bus bars [Nice easy way as to not have change any cabling across the roof].

    Or this will negate the 24v (less cable thickness advantage), run from the solar banks?

    If so, what about (at the 4-6mtr), joining the 4 x 12volt banks into 2 feeds of 24v at the roof level [Will require a cable box enclosure] and then the remaining 7-8mtr run is all 24volts...?


    Thanks...

  6. #26
    Join Date
    Jun 2007
    Location
    Williams Lake, BC
    Posts
    2,071

    Default Re: About to buy new Batteries - not sure if my set up is correct to start with

    the simplest way to describe this is to hook the negative of panel #1 to the positive of panel 2 and the pos of panel 1 and the neg of anel 2 to the buss bar. Hope this makes sense. try drawing it out.
    In this way the voltage will be 12 + 12 = 24 from 2 panels.

    hth
    100% Off Grid @ 51* 46' N lat 124* 44' W long

    New House system: MX-60 w RTS, 2 - 120 W 12v PVs, 2 - C&D AT-15P AGM 24V 950Ah, Cotek ST1500W inverter, TBS 30a-24v Omni-charger, Honda Eu3000is, CL 150 coming out of a box, coming - 2 arrays @ 2240W

    Guest cabin system: 3 - 70W panels to SB 2000e CC, with 2 - 100 ah 12v SAFT wet NiCd's , 600W TSW Inverter

    Mothballed :Absolyte AGM 1055 Ah 12 v battery, XBM w/ Palm Vx data recorder, 3500 W Mitsubishi genset, TC40 (12V) charger ...

  7. #27

    Default Re: About to buy new Batteries - not sure if my set up is correct to start with

    You are now going with a 24 Volt system, correct?
    You will need an array capable of at least 35 Vmp. Having the panels wired as 12 Volts won't even nudge the battery, much less charge it.

    Normally you get panels and they have polarized MC4 connectors on them. Plug two together and you get a series string of two panels that produces 24 Volts nominal.
    Put four in series by this manner and you get a nominal 48 Volt string. Parallel five such strings together and feed it to an MPPT type charge controller. There's your twenty panels used. The output will be fine for charging a 24 Volt system.

    And did anyone mention the need for fuses/breakers on each string?
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  8. #28
    Join Date
    Jul 2012
    Location
    Gold Coast Australia
    Posts
    14

    Default Re: About to buy new Batteries - not sure if my set up is correct to start with

    Quote Originally Posted by westbranch View Post
    the simplest way to describe this is to hook the negative of panel #1 to the positive of panel 2 and the pos of panel 1 and the neg of anel 2 to the buss bar. Hope this makes sense. try drawing it out.
    In this way the voltage will be 12 + 12 = 24 from 2 panels.

    hth
    Thank you for that advise! Very simple and i get it straight away.

    Cheers,
    Alan.

  9. #29
    Join Date
    Jul 2012
    Location
    Gold Coast Australia
    Posts
    14

    Default Re: About to buy new Batteries - not sure if my set up is correct to start with

    Quote Originally Posted by Cariboocoot View Post
    You are now going with a 24 Volt system, correct?
    You will need an array capable of at least 35 Vmp. Having the panels wired as 12 Volts won't even nudge the battery, much less charge it.

    * Hi Cariboocoot (glad to see your still here), yes starting to go 24v.

    * With this "array capable of 35vmp and the panesl wired as 12volts.." What is this 35vmp?


    Normally you get panels and they have polarized MC4 connectors on them. Plug two together and you get a series string of two panels that produces 24 Volts nominal.
    Put four in series by this manner and you get a nominal 48 Volt string. Parallel five such strings together and feed it to an MPPT type charge controller. There's your twenty panels used. The output will be fine for charging a 24 Volt system.

    * The 'big panels' i have are 5 a piece, not 5 'big panels' by 4 individual solar panels...
    * We don't have the money to buy a MPPT type charge controller. I have read about the MPPT controllers and whilst they can 'distribute' the panel(s), * maximum input to the batteries etc, it IMO and in our case, is not cost effective.

    And did anyone mention the need for fuses/breakers on each string?
    * Yes, i will be looking at that. At the moment, I have a fuse/breaker on the input - after the bus bars - to the PL60 and then the same after the PL60.
    * So i will once i get the wiring to 24volts, have a fuse/breaker on the 'new' two feeds.

  10. #30

    Default Re: About to buy new Batteries - not sure if my set up is correct to start with

    Quote Originally Posted by obba View Post
    * Yes, i will be looking at that. At the moment, I have a fuse/breaker on the input - after the bus bars - to the PL60 and then the same after the PL60.
    * So i will once i get the wiring to 24volts, have a fuse/breaker on the 'new' two feeds.
    Two feeds? According to my calculations you will have five feeds to the combiner and that means five fuses or breakers; one on each string.
    You must not combine strings and then connect to circuit protection. It will not be safe for the reasons we use circuit protection there.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

Similar Threads

  1. Correct way to parallel batteries
    By Volvo Farmer in forum General Solar Power Topics
    Replies: 4
    Last Post: January 6th, 2012, 17:58 PST
  2. Off grid - generator and batteries to start
    By jakenshake in forum Solar Beginners Corner
    Replies: 40
    Last Post: June 2nd, 2011, 17:47 PDT
  3. Is my thinking correct?
    By in_dmand in forum Solar Beginners Corner
    Replies: 16
    Last Post: March 15th, 2011, 12:10 PDT
  4. Is my logic correct?
    By bradw in forum Solar Beginners Corner
    Replies: 1
    Last Post: April 5th, 2010, 12:28 PDT
  5. Is this correct?
    By Telco in forum General Solar Power Topics
    Replies: 15
    Last Post: February 13th, 2008, 6:54 PST

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •