Results 1 to 9 of 9

Thread: how to connect 12 250 watt panels together

  1. #1

    Default how to connect 12 250 watt panels together

    dears
    i am going to install a ongrid system with a 12 250 watt panels VOC 45V , with a 3.6kw inverter , please advise the right way to connect the panels (diagram) and the precautions to avoid any mistakes
    THANK YOU
    ABDALLA MAHMOUD
    EGYWATT

  2. #2

    Default Re: how to connect 12 250 watt panels together

    Welcome to the forum.

    We'll need a bit more information first. Mainly what the specifications are on the inverter. Is this a grid tie unit or is it battery based?

    A grid tie inverter will have information about its minimum and maximum input Voltage which is key to wiring the solar panel array properly.

    A battery-based inverter (either off grid or hybrid grid tie) is another matter as it will have a battery Voltage and capacity which are necessary to know for selecting a proper charge controller and wiring the solar panel array.

    The complete specifications of the panels would be helpful too, just to make sure minimum Voltages are met and any fusing is noted as well as getting the wire size right. Distance from the array to the inverter or controller is important to that too.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  3. #3
    Join Date
    Apr 2010
    Location
    Austin, TX, USA
    Posts
    1,542

    Default Re: how to connect 12 250 watt panels together

    Quote Originally Posted by egywatt View Post
    dears
    i am going to install a ongrid system with a 12 250 watt panels VOC 45V , with a 3.6kw inverter , please advise the right way to connect the panels (diagram) and the precautions to avoid any mistakes
    THANK YOU
    ABDALLA MAHMOUD
    EGYWATT
    It really depends on a lot of things. If your inverter manufacturer has an on line string sizing tool, that's where you should start. You should get that information before you buy anything; it's possible that you cannot connect 12 panels to that inverter. If the string sizer tells you (for example) that the minimum string length for that module, that inverter, and conditions at your location is 7, then your choices are 7 and 14 (or 8 and 16, maybe). One string of 12 is probably not going to work; that would be an uncorrected string Voc of 540V. If your inverter has a maximum input voltage of 600V as a lot of them do, there's a good chance that you'd go over that on a cold morning, which could damage the inverter and void the warranty.

    At any rate, there is some homework you should do before you buy any gear.

  4. #4
    Join Date
    Mar 2006
    Location
    SF Bay Area (California)
    Posts
    16,872

    Default Re: how to connect 12 250 watt panels together

    I think ggunn intended to type MPPT Charge controller string sizing tool (here is one from MorningStar).

    -Bill
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

  5. #5
    Join Date
    Apr 2010
    Location
    Austin, TX, USA
    Posts
    1,542

    Default Re: how to connect 12 250 watt panels together

    Quote Originally Posted by BB. View Post
    I think ggunn intended to type MPPT Charge controller string sizing tool (here is one from MorningStar).

    -Bill
    Did I? I don't think so. The OP says he wants to build a grid tied system, not a system with a charge controller (batteries). An MPPT charge controller is going to require different stringing; there aren't any that accept 600VDC, are there?

    Most inverter manufacturers have their own string sizing tools. Here is SMA's: http://www.sma-america.com/en_US/pro...ny-design.html

  6. #6

    Default Re: how to connect 12 250 watt panels together

    Mea culpa!
    I didn't see that "ongrid system" in the first post and confused the issue.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  7. #7
    Join Date
    Mar 2006
    Location
    SF Bay Area (California)
    Posts
    16,872

    Default Re: how to connect 12 250 watt panels together

    Sorry, missed the On-Grid Inverter... When you typed "inverter manufacturer"--I defaulted to Off Grid instead Grid Tied.

    -Bill
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

  8. #8
    Join Date
    Feb 2010
    Location
    South of Erie, North of Pittsburgh PA
    Posts
    894

    Default Re: how to connect 12 250 watt panels together

    You should post the brand name and model number of the solar panels and give the colfest temp you have at your location. It would be easy then to figure if your panels would work on a 600 volt inverter. solarvic
    16 KC 158G & 3 KD185GX-LPU panels on Fronius IG PLUS 3.0-1 inverter and 14 SHARP NDU3A & 1 KD185GXU panel on FRONIUS IG-3000 inverter. All mounted on pole top racks. Retired and enjoying it!!

  9. #9
    Join Date
    Apr 2010
    Location
    Austin, TX, USA
    Posts
    1,542

    Default Re: how to connect 12 250 watt panels together

    Quote Originally Posted by solarvic View Post
    You should post the brand name and model number of the solar panels and give the colfest temp you have at your location. It would be easy then to figure if your panels would work on a 600 volt inverter. solarvic
    We would need the inverter info as well; different inverters have different DC input voltage windows. It would also be useful to get the highest average high temperature he would see and the type of racking he will be using so that we could tell if his voltage would be high enough on hot days to keep the inverter running.

Similar Threads

  1. Thoughts on Sharp Mono 240 watt panels at $1/watt?
    By chetwynd in forum Solar Product Reviews & Opinions
    Replies: 9
    Last Post: February 22nd, 2012, 13:05 PST
  2. Connect panels
    By Ken Floyd in forum Solar Beginners Corner
    Replies: 2
    Last Post: July 28th, 2011, 15:40 PDT
  3. Best way to connect grid tie panels to off grid system
    By wingnutter in forum Advanced Solar Electric Technical Forum
    Replies: 7
    Last Post: July 4th, 2010, 10:39 PDT
  4. Portable quick connect 5x20watt panels?
    By whackamole in forum Solar Beginners Corner
    Replies: 10
    Last Post: July 6th, 2008, 1:36 PDT
  5. 2 - 100 watt panels with a 50 watt panel
    By stooper2 in forum General Solar Power Topics
    Replies: 5
    Last Post: August 20th, 2007, 8:18 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •