Originally Posted by
niel
i wouldn't do that on mine, but who am i? think for a second as they warrant the batteries for 1yr. the batteries will easily last 1yr with abuse from eqing. many moons ago they did not even give an eq spec and that's because eqing could pop the vents. my recommendation would be an extended absorb charge if you don't suspect any problems with the batteries. one should exercise caution when you do go to do an eq charge and you should be there to listen for vents popping open. it wouldn't be real loud, but if you were to hear it then shut down the eq charging immediately. this does not save the day as some water escaped when it popped open.
most needs of eqing are from inequalities between the batteries possibly due to connections, unequal wiring, or minor differences in the batteries which should not be if all were purchased new in the same batch. track the voltages now and then (every 1 to 3 months would be good) of the individual batteries during a rest period. if there's a consistent irregularity in the voltages then try switching a low battery (by voltage) with a high battery. if that battery slot still shows up low then suspect the wires or connections to that slot otherwise the switching could physically force an equalization.
i need to do this for mine too as i'm long overdue.
of course be sure the voltages are set correctly for charging in the first place. i try for the middle of the road on the charge voltage range. the extended absorb charge, should you opt for that should go to the charge voltage top end of 2.4v per cell and that's before temp compensation.