    Default New 24 volt system AGM question

    I recently acquired a used XW4024, midnite E-panel, and a set of 12 Enersys Powersafe 12v155f's(4 year old batteries in excellent condition). For the price I couldn't back away being a beginner and all. $6.00 per battery and $900 for the inverter, Dist. panel, controller, battery rack,and wiring. If I screw up, I spent more in fuel and time then parts.
    The batteries are set up in 6 strings @ 155ahr per string for a total of 930 ahr @ 24 volts. I know less strings are better, but dirt cheap is good too.

    I have all the specs programmed as far as charger rates, voltages etc. That much I'm OK with.

    My AGM question is: Looking at the enersys performance spec sheet, They list capacities down to 1.60Vpc=9.6 Volts per battery=19.2 volts in my 24 volt system.
    These would have to be voltages under load, Correct?
    Cause if not, These batteries would be very very dead and ready for the crap yard after 1 or 2 deep discharges.

    Thanks
    Topper

  2. #2
    Join Date
    Jun 2003
    Location
    pittsburgh, pa
    Posts
    9,221

    Default Re: New 24 volt system AGM question

    that's taking them quite far down in any case, but i think it is a loaded voltage.
    voltage drop calculator http://www.wind-sun.com/ForumVB/showthread.php?t=29


    NIEL (not employed by naws)

  3. #3
    Join Date
    May 2010
    Location
    Weyburn SK
    Posts
    101

    Default Re: New 24 volt system AGM question

    Discharge Rates in Amperes to 1.60Vpc at 25°C/77°F
    Minutes Hours
    TYPE 5 10 15 20 25 30 35 40 45 50 55 1 1.5 2 2.5 3 4 5 6 7 8 9 10 12 24
    12V155FS 498.0 352.8 280.6 239.7 210.1 186.3 167.7 152.1 139.3 128.6 122.0 109.7 79.7 63.2 52.5 45.1 35.4 29.3 25.1 22.0 19.7 17.6 16.1 13.6 7.25

    Cut n Paste didn't worjk so well. Sorry.

  4. #4
    Join Date
    Jun 2007
    Location
    Williams Lake, BC
    Posts
    2,068

    Default Re: New 24 volt system AGM question

    there should be a whole set like that are starting at ~ 1.9VPC down to ~ 1.60VPC. they are meant for doing load (depletion) tests... you don't want to go there unless you are willing to lose the set if it is failing, read their manual about periodic tests.

    Good catch
    100% Off Grid @ 51* 46' N lat 124* 44' W long

    New House system: MX-60 w RTS, 2 - 120 W 12v PVs, 2 - C&D AT-15P AGM 24V 950Ah, Cotek ST1500W inverter, TBS 30a-24v Omni-charger, Honda Eu3000is, CL 150 coming out of a box, coming - 2 arrays @ 2240W

    Guest cabin system: 3 - 70W panels to SB 2000e CC, with 2 - 100 ah 12v SAFT wet NiCd's , 600W TSW Inverter

    Mothballed :Absolyte AGM 1055 Ah 12 v battery, XBM w/ Palm Vx data recorder, 3500 W Mitsubishi genset, TC40 (12V) charger ...

  5. #5
    Join Date
    Mar 2006
    Location
    SF Bay Area (California)
    Posts
    16,815

    Default Re: New 24 volt system AGM question

    At least 20 years ago when I was designing equipment for Telephone Company use--They wanted good quality product-But expected it to run to destruction in an emergency situation.

    We had many arguments about if our system should down down >55C (131 F) or keep running (phone guys told us to keep running--we decided to shut down).

    Eventually, one of our systems had an electrical fire (capacitor failed shorted). System did shut down (fire was right under our temp sensor). Fire department came, broke through (very expensive) fire/security doors at the unattended central office, and found our system had shut down and stopped burning long before.

    In the end, that battery specification is, probably, an emergency operational specification (discharge to destruction is OK).

    In general, discharging below 11.5 volts (23 volts for 24 volt system) is probably about as low as you would like to go in normal operation (perhaps a few second to few minute time delay to allow surge current). Going to 10.5 volt (21 volt) is pretty much going to shorten the life of a new battery bank, and probably will kill a battery bank with more than a couple of years of service.

    -Bill
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

  6. #6
    Join Date
    May 2010
    Location
    Weyburn SK
    Posts
    101

    Default Re: New 24 volt system AGM question

    Thanks for your interpretations.
    I think I'll leave the low batt cut out at 22.5-23 volts. I wouldn't mind this set lasting me at least a few years. I'm running as a UPS/backup power only till I get solared up.

  7. #7
    Join Date
    Sep 2006
    Location
    Willits, CA
    Posts
    4,962

    Default Re: New 24 volt system AGM question

    Once you discharge a bank really deeply, you end us "reverse charging" the lowest capacity cell in the system.

    When that happens, the battery (however many cells in the case, 1,3, or 6) is killed, and you have to replace it,

  8. #8
    Join Date
    May 2010
    Location
    Weyburn SK
    Posts
    101

    Default Re: New 24 volt system AGM question

    Well. I am very happy with my purchase. We have had some wicked weather June 26th, June 28th and July 1st. 2 4-6 hr outages and a couple brown outs for an hour or so due to high winds, hail and twisters.
    Batteries performed extremely well. Inverter worked and the wife didn't even know the power went out.(except for the digital clock on the stove).
    Thank-you to you all.
    GT / Backup
    XW4024, Magnum E-panel, SCP , 12-enersys 12V155F (24 volt @ 930Ahr), 7500W gas genset tied to generator input(backup for the backup)

Similar Threads

  1. Add Xantrex C60 controller (set to 12 volt) to 24 volt system
    By James in forum Advanced Solar Electric Technical Forum
    Replies: 26
    Last Post: April 30th, 2012, 8:43 PDT
  2. 48 volt wind generator to charge 24 volt system?
    By krussell in forum Wind Power Generation
    Replies: 0
    Last Post: February 22nd, 2010, 21:54 PST
  3. Running 10.5 volt modem on 12 volt system
    By paulstamser in forum Off Grid Solar & Battery Systems
    Replies: 12
    Last Post: September 21st, 2009, 14:35 PDT
  4. Charging 24 volt system with a 12 volt charger-
    By rickeolis in forum Advanced Solar Electric Technical Forum
    Replies: 22
    Last Post: March 25th, 2008, 14:48 PDT
  5. 12 or 24 volt...... that is the question
    By azqualbuster in forum General Solar Power Topics
    Replies: 3
    Last Post: March 19th, 2007, 9:11 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •