Re: OFF-Grid - transfer Switch with 2 inveters and Genset

Originally Posted by
BB.
TSW inverters can share a common ground referenced neutral
Personally, I think I would just keep both small/large inverter outputs isolated (breaker boxes/wire runs) unless they support grounded neutrals. emails off to both suppliers.
In theory, you could have two isolated (TSW usually) inverters (small/large) powering a 120/240 VAC split phase fuse box. The "A" phase hot to neutral would be your small 120 VAC inverter and the "B" phase would be your Large 120 VAC inverter.
-Bill
thanks Bill, yes both are TSW inverters, and as you say they should be able to share a common ground referenced Neutral...
I did look at the Magnum inverter but there is no need for 220V, the gen I have are 110V only (inverter model), 4000w is way above my needs, and the cost...
You may notice similarities as I have refered to Steve's post several times.
I made some clarifying changes to that chart.
2Xfer switches.pdf