Page 1 of 2 12 LastLast
Results 1 to 10 of 11

Thread: need help with generator

  1. #1
    Join Date
    Feb 2012
    Location
    Houston TX
    Posts
    13

    Default need help with generator

    smooth sailing until generator hookup,
    here is what i've got, vfx 2812 x 2, (hooked up in series/parallel stack) flexmax 80 x 2, psx auto 240 trans, mate2 , hub4, 380ah 6vlt x 16. sharp solar tiles x 32. champion 7500 gen wired to both (IN) legs in ac panel.
    I get a hum in both inverters and redlight error (solid red) i've gone over my wiring multiple times and cant figure out the problem, dc and ac works fine, it throws the error with generator off but wired, when unwired system works correct again. input breakers, bypass breakers, hot legs in 1 and 2, hot legs out 1 and 2 seem to be wired correct.
    can anyone help?
    Thanks

  2. #2

    Default Re: need help with generator

    Welcome to the forum.
    You say series/parallel - as per Page 27 in the manual?
    First inverter designated as "master" and second as "slave" (HUB ports 1 and 2 respectively). First inverter using black AC line for input and output (and autotransformer) and second using red AC line.
    Now, without the generator connected the two inverters function off batteries and supply 240 VAC up to 2800 Watts?
    Or is the master inverter only functioning with the slave never turning on?

    Next, check the output lines from the generator. That model does not have a neutral-ground bond built in. This bond should only occur at the final AC out from the transformer, feeding the service panel.

    If the gen wiring is disconnected at the gen does it work? Or only if disconnected at the inverter inputs?

    It sounds as though the generator wiring is picking up AC hot from one inverter side and feeding it into the other. Try disconnecting the autotransformer and seeing if the problem persists (no loads, no generator running - just wiring).
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  3. #3

    Default Re: need help with generator

    Link to wiring diagram that includes the autotransformer: http://www.outbackpower.com/pdf/wiri...1-00_REV_A.pdf
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  4. #4
    Join Date
    Feb 2012
    Location
    Houston TX
    Posts
    13

    Default Re: need help with generator

    [Thanks for the reply, yes to pg 27, slave assignment and hub assignment,slave has blinking green light which i think is good, with ( gen unplugged) and input breakers on, both inverters have flashing yellow light waiting for ac which i also believe is good, but it does sound like cross wiring, I wired system from ps2 ac and ps2 dc diagrams, system is very close except instead of dual output and dual bypass breakers i used single breakers x 2 of each could this be the issue ? it seems strange that with everything hooked up, it faults by just plugging in the genn that is not even running. thanks again for info, i will give it another shot in the morning.]

  5. #5

    Default Re: need help with generator

    Particularly check to make sure there is a neutral-ground bond. Otherwise the neutral can become "hot" and back-feed through the gen windings causing the inverters to see a low AC in Voltage.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  6. #6
    Join Date
    Jul 2007
    Location
    Ontario Canada
    Posts
    717

    Default Re: need help with generator

    Not sure if this is pertinent but I had the neutral from my T240 autotransformer end up carrying current when gen charging. Not OB but Xantrex stuff. The L1 and L2 were not balanced, one leg showed full current expected, one leg very little current measured...the remainder was carried back to the genset via the neutral. This didn't affect my 10kw genset but made my 5kw genset act very unbalanced. By isolating the neutral and just feeding 240vac to the autotransformer the problem dissapeared and things functioned properly.

    Just wondering why is there an autotransformer in the mix when there's 2 inverters putting out 240vac.

    Ralph

  7. #7

    Default Re: need help with generator

    Quote Originally Posted by Ralph Day View Post
    Not sure if this is pertinent but I had the neutral from my T240 autotransformer end up carrying current when gen charging. Not OB but Xantrex stuff. The L1 and L2 were not balanced, one leg showed full current expected, one leg very little current measured...the remainder was carried back to the genset via the neutral. This didn't affect my 10kw genset but made my 5kw genset act very unbalanced. By isolating the neutral and just feeding 240vac to the autotransformer the problem dissapeared and things functioned properly.

    Just wondering why is there an autotransformer in the mix when there's 2 inverters putting out 240vac.

    Ralph
    Ralph;

    It's an Outback thing.
    The autotransformer allow the two inverters to supply either 2800 Watts on 240 VAC or 5600 Watts on either leg of 120 VAC. There's other ways to arrange them; Outback has a lot of wiring diagrams to go with the many possible configurations.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  8. #8
    Join Date
    Feb 2012
    Location
    Houston TX
    Posts
    13

    Default Re: need help with generator

    Thanks for all the help everyone, Ive been in wire chaos for the last few days, as for the added psx 240 I was told was good for balancing / getting more out of the pair of inverters, I am much closer, I now have everything running smooth except I must shut off the 240 trans when the gen is running or I end up with 480, This wouldnt be such a big thing, except that will defeat any chance of auto gen with the atkinson gscm. I spent alot of time searching for a gen with auto choke, I didnt see the purpose of auto gen if you have a manual choke, but I am back to sqaure one with that.
    Quote Originally Posted by Ralph Day View Post
    Not sure if this is pertinent but I had the neutral from my T240 autotransformer end up carrying current when gen charging. Not OB but Xantrex stuff. The L1 and L2 were not balanced, one leg showed full current expected, one leg very little current measured...the remainder was carried back to the genset via the neutral. This didn't affect my 10kw genset but made my 5kw genset act very unbalanced. By isolating the neutral and just feeding 240vac to the autotransformer the problem dissapeared and things functioned properly.

    Just wondering why is there an autotransformer in the mix when there's 2 inverters putting out 240vac.

    Ralph

  9. #9
    Join Date
    May 2006
    Location
    Florida, USA
    Posts
    1,232

    Default Re: need help with generator

    I know the Outback diagram is showing the auto transformer on output for balancing the 120 v loads but many autotransformers and just about all isolation transformers are are not 1:1 turns ratio. The are typically 1:1.02 to 1:1.05 beween the two winding. This is done to make up the transformer loss. This would upset the balance slightly when trying to do load balancing.

    You might check the open circuit (unloaded, with temporary floating neutral on transformer) voltages between the two windings to see if it is equal.

  10. #10
    Join Date
    Sep 2006
    Location
    Willits, CA
    Posts
    4,963

    Default Re: need help with generator

    If you are seeing 480Vac, you have something out of phase, is my first guess.

    Consider having your genset just power a charger for the battery bank, not wired into the AC mains, if you can't get it working any other way.

Similar Threads

  1. Wiring a generator to a Grundfos IO 101 Generator Box
    By eagle1tx in forum Solar Water Pumping
    Replies: 2
    Last Post: May 26th, 2011, 5:43 PDT
  2. Xantrex XW, Generator not being qualified until load applied to generator
    By Les Nagy in forum Off Grid Solar & Battery Systems
    Replies: 14
    Last Post: July 27th, 2010, 17:04 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •