  1. #1

    Default charge controller readings

    I have a trace C40 controller that I have connected to 6 siemens 17v 75 watt panels. The panels are wired series parallel. This feeds into a 24v 340 amp hour battery bank. I have just set this up. I thought that the panels would dictate the current being fed to the batteries but it seems to be the other way around i.e. the batteries seem to be restricting the panel output. Yesterday was a very sunny day and the C40 progressed from about 4 amps in the morning to 11 amps at midday but the watts always progreesed at a ratio so that the voltage stayed just over 24v. eg 11amps/ 268 watts = 24.3 volts. The reading at the panels is about 2v higher than at the C40. My multimeter won't measure over 10 amps so I didn't check the amps at the panel. When I disconnected the C40 from the batteries the voltage stayed much the same. How do I get the voltage up so that it charges the batteries?

  2. #2

    Default Re: charge controller readings

    Let's see. Six 75 Watt panels is 450 Watts. Less a typical 77% efficiency derating is 346 Watts. Divide by 24 Volts nominal = 14 Amps peak current, which is 4% of 340 Amp hours. You're seeing 11 Amps, which is only 3%. You're going to run out of sun before that array manages to get the battery Voltage up to Absorb level.

    Solution: get enough panels to charge the battery bank. You've got about 1/2 the amount needed.
    Before you do that, find another way to charge the batteries before it's too late.

    Just to cover bases, check the Isc on each panel and the insolation too. Watch out for long wire runs from array to controller or too small wire size; either can eat up Voltage when under load.

    Oh, and you shouldn't disconnect a controller from the batteries if there are panels connected to the input. It can be bad for the controller.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

  3. #3

    Default Re: charge controller readings

    I have a generator as well which we have been using for several months to keep the batteries up. If I get the batteries up to absorb with the generator then will the panels finish them off?

  4. #4

    Default Re: charge controller readings

    Quote Originally Posted by cargillfarm View Post
    I have a generator as well which we have been using for several months to keep the batteries up. If I get the batteries up to absorb with the generator then will the panels finish them off?
    They should, providing that 17 Volt panel spec is the Vmp and not the Voc.
    When you're reading 11 Amps output on the charge controller check the Voltage coming in to it from the panels. Hopefully it will be around 34 Volts.
    Four 175 Watt panels, OB MX60, 232 Amp hrs, OB 3524, Honda eu2000.

    Ohm's Law: Amps = Volts / Ohms
    Power Formula: Watts = Volts * Amps

Similar Threads

  1. perplexing charge controller readings
    By lazza in forum Off Grid Solar & Battery Systems
    Replies: 31
    Last Post: December 12th, 2011, 6:13 PST
  2. New Controller, new voltage readings?
    By bmet in forum Solar Beginners Corner
    Replies: 2
    Last Post: May 10th, 2011, 21:35 PDT
  3. float (maintenance) charge without a charge controller
    By wagoneer in forum Solar Beginners Corner
    Replies: 8
    Last Post: August 27th, 2010, 13:40 PDT
  4. Charge Controller - Bulk Float Charge?
    By tkc100 in forum Advanced Solar Electric Technical Forum
    Replies: 25
    Last Post: March 28th, 2010, 21:43 PDT
  5. Charge set points -SW5548 vs TC60 charge controller
    By dbertheau in forum Grid Tie and Grid Interactive Systems
    Replies: 7
    Last Post: October 7th, 2008, 21:07 PDT

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •