#1 I've read that the NEC says that my inverter should not be above my basement battery box, yet the paperwork that came with the inverter says that I should have cables not exceeding 5 feet in length. Since practicality dictates that the battery box for weight reasons needs to be on the floor. And the inverter is mounted to plywood on the wall like most electricians prefer. How can I satisfy the NEC about this and still keep the inverter within 5 feet? If I pull the box out from the wall 18" so that the inverter is not DIRECTLY above it, has the NEC been satisfied?
#2 My battery box has six golf cart batteries, three strings in parallel. To date I have no fuses between the strings. If I were to install fuses between the strings, then either they would have to be within the box (nope - will NOT do that!), or I'd have to have six leads exiting the box to external fuses on the wall (kinda sloppy and lots lots more resistance). Neither option is one I want to do. How much risk just to fuse the positive master lead to the inverter and forget the fuses between strings? Or...how else to do it?
Thanks for any helpful advice...